Q&A: How to set up IPT-2CH?

IPT-2CH can control two heaters separately, but please note that the current (including instantaneous current) of each heater cannot exceed 2.5A.
Input: 100~240Vac 50/60Hz
Output: 100~240Vac 50/60Hz 500W Max
Please make sure that the heater can be turned on automatically after it is energized, it does not need to manually press the button to turn on.

For example: You want to use two heating pads to maintain the temperature at two locations. Heating pad A is maintained at 40F~45F. If the temperature reaches/below 38F or reaches/higher than 48F, an alarm will be triggered.
Heating pad B is maintained at 50F~53F. If the temperature reaches/below 47F or reaches/higher than 56F, an alarm will be triggered.
Please insert heating pad A into work1 socket and heating pad B into work2 socket. The probe inserted in the P1 port is placed in the A environment. The probe inserted in the P2 port is placed in the B environment.

Parameter code table:

Please set:
CF=F
ST1=40
SP1=45
AH1=48
AL1=38
CA1=0
ST2=50
SP2=53
AH2=56
AL2=47
CA2=0
ALM=ON
When the temperature of environment A reaches or falls below 40F (ST1), IPT-2CH will turn on the heating output of work1. Turn off when the temperature reaches 45F (SP1).
When the temperature of environment B reaches or falls below 50F (ST2), IPT-2CH will turn on the heating output of work2. Turn off when the temperature reaches 53F (SP2).