Q: How to set ITC-306T?

A: Here are some tips for ITC-306T temperature controller settings:

‘PV’ is current temperature

‘SV’ is setting temperature ‘TS’ is your target value

‘DS’ is the differential value ‘CA’ is the calibrated value

‘CF’ is the unit of temperature (°C or °F)

‘TR’ is time setting ( 0:off / 1:on )

There will be 2 situations when you use this thermostat.

  1. If you only need to control a same temperature range the whole day.

For example, you need to keep the temperature within 22°C~25°C, then set the controller as follow:

TS1=25, DS1=3, CA=0, CF=C, TR=0

With this setting, when the PV actual temperature is lower than TS1-DS1=25-3=22C, the work light will turn on and your heaters will start outputting, and it will stop when the temperature reaches to 25°C (TS1/SV);

2.If you need to control different temperature range during day and night.

For example, during 8:00~18:00, keep temperature within 22°C~25°C, during 18:00~8:00, keep temperature within 27°C~25°C

TS1=25, DS1=3, CA=0, CF=C, TR=1, TS2=27,DS2=2, TA=8, TB=18, TH=the hour of the current time when you set , TM= The minute of the current time when you set.

During (8:00~18:00) TA~TB, the thermostat will work with TS1 and DS1. During (18:00~8:00) TB~TA, the thermostat will work with TS2 and DS2.

Hold Set button for more than 3s to enter the set menu, use up and down button to adjust the value, press set button to confirm the parameter and enter another parameter. After finish all settings, hold Set button 3s again to save them.

Hello,
We have tried to set up our ITC 306 for fish pond. We want it to come on at 8am and turn off at 10 pm at night besides the temperature controls.
But we can’t figure this out?

Tricia

Hello,
Sorry it doesn’t have this feature. It cannot be set to stay off for one of the time periods.

We don’t want the pump running through the night is there a way to control that?

Please note that the ITC-306T only has a heating function.
The ITC-306T switches the output on and off according to the temperature change and the set value, it has 2 time periods to control different temperature ranges. When the temperature reaches the set value, the outputs will be switched on. Its outputs cannot be disabled.
Perhaps you could set the target temperature for the second time period to a minimum in order to ensure that the current temperature is higher than the target temperature, so that the ITC-306T will not switch on the outputs.

Hi there ive bought 2 itc 306a wifi tempreture cintrollers ive bought them to control the tenpretures in my python vivarium i have placed one sensor in one half of the vivarium and the other sensor in the other half of the vivarium i wanted it control the the temp in hot side to 32c and in the cold end monitir the temp didnt exceed 24c im currenly using a heat mat and a sepeate ciramic heater lamp to heat the tempretures in the hot side to 32c and have nothing controlling temperature in cold side i keep getting this e4 error which i believe is due to temperature diference between the two probes can this device be used to control the temperatures in two seperate areas in one tank if so how come i keep gettin this e4 error all time or does it only controll one area and the probes have to be installed side by side in same area not in seperate halfs of the vivarium if anyone can help please email garethkwalker4183@gmail.com any help will be greatfully recieved im based in uk so only understand english thanks guys