I live in Europe and I bought the IPB 16S for my heating element of 2000W and an Iwaki pump from my brewery. The seller wrote to me I only have to use a transformer for going from 110V to 220V but I don’t believe this is correct. The mump did work indeed but after starting the heating element, it went wrong an I think I blew op the transformer.
Can somebody tell me what I should do in order to make this work?
Sorry, the IPB-16S only has US version. The GFCI plug can only use 120V .
Heat:15A for 120 VAC (1800W)
PUMP: 8A for 120VAC(resistance load)
Please do not use 220V power supply.
you put a transformer between the controller and the net to go from 230v to 120v
you put an adapter (from a computer f.i.) and a solid state relais between the controller and the heating element.
you put the heating element on te 230v network
The only disadvantage (I think) is the complexity of it all and the fact that there is a delay between the controller and the heating element.