Hi, I have an inkbird itc100vh and I am running it in Manual mode… does this mode get affected by the measured temperature or not?
I mean, I set the percentage of the output to 50%, and Ctl time to 4 seconds, and the temperature to 20°C, in Manual mode… the measured temperature is 15°C, and the controller is working 2 secs and does not work 2 secs which is good and expected… but when the desired temperature is achieved (20°C), the controller still works the same… I would expect it to stop working when the temperature is reached…
Thanks
Hello,
Sorry, if in manual mode, it works according to the manually set output %, it will not stop the output according to the target temperature.