Hi,

I have a question regarding the PID temperature control 106. I made an unconventional oven that has two elements inside. My issue with the temperature control is when i set it to 50 degrees, it goes up to 400 degrees. It doesn’t matter where i set the temperature at it will go up to 400 degrees. Are there any tips that you guys recommend or am i doing something wrong?

---

<div class="post-metadata">

**Author:** ![Tania](https://yyz1.discourse-cdn.com/flex031/user_avatar/community.inkbird.com/tania/32/88_2.png) [@Tania](https://community.inkbird.com/u/Tania)\
**Post date:** [April 9, 2022, 2:34am UTC](https://community.inkbird.com/t/temperature-control/464/2 "2022-04-09T02:34:52Z")

</div>

Hello,  
May I know the model you purchased is ITC-106VH/ ITC-106VL/ ITC-106RH/ ITC-106RL?  
What is the wattage and voltage of the oven?

---

<div class="post-metadata">

**Author:** ![Carlos72](https://avatars.discourse-cdn.com/v4/letter/c/ecb155/32.png) [@Carlos72](https://community.inkbird.com/u/Carlos72)\
**Post date:** [April 9, 2022, 3:19am UTC](https://community.inkbird.com/t/temperature-control/464/3 "2022-04-09T03:19:47Z")

</div>

Hi

Its a ITC-106VH. The braker is 240v and 20 amps.

---

<div class="post-metadata">

**Author:** ![Tania](https://yyz1.discourse-cdn.com/flex031/user_avatar/community.inkbird.com/tania/32/88_2.png) [@Tania](https://community.inkbird.com/u/Tania)\
**Post date:** [April 11, 2022, 2:06am UTC](https://community.inkbird.com/t/temperature-control/464/4 "2022-04-11T02:06:56Z")

</div>

Please note that the ITC-106VH requires an SSR to be connected.  
SSR electric current version calculation method: Device current x 2.5  
For example, if the device is 20A, then the SSR is best to use ≥50A  
Please check if the connection is correct  
 ![image](https://canada1.discourse-cdn.com/flex031/uploads/inkbird1/original/1X/390ae250f1e3a17559172e83eae30ee4113b5ac8.png)

If there is no problem with SSR version and connection, maybe you can try the self-tuning mode:  
SV=50  
CtrL= AT (self-tuning)  
Run= dm (manual inhibit)  
Others are factory defaults

Can it work?