# ITC-308 wifi starting cooling cycle too early

**URL:** https://community.inkbird.com/t/itc-308-wifi-starting-cooling-cycle-too-early/150768
**Category:** Uncategorized
**Created:** [April 17, 2024, 4:22am UTC](https://community.inkbird.com/t/itc-308-wifi-starting-cooling-cycle-too-early/150768 "2024-04-17T04:22:27Z")
**Posts on this page:** 4
**Page:** 1

<div class="post-metadata">

### Author: ![npaashish](https://avatars.discourse-cdn.com/v4/letter/n/f17d59/32.png) [@npaashish](https://community.inkbird.com/u/npaashish)
#### Post date: [April 17, 2024, 4:22am UTC](https://community.inkbird.com/t/itc-308-wifi-starting-cooling-cycle-too-early/150768/1 "2024-04-17T04:22:27Z")

</div>

Hello everyone,  
I have set 26.5 degree celcius as required temperature and cooling difference is 1.0 degree celcius but cooling start as soon as it hit 26.5 or above. Shouldn’t it wait until 27.5 or above?  
Thanks in advance.

---

<div class="post-metadata">

### Author: ![Tania](https://yyz1.discourse-cdn.com/flex031/user_avatar/community.inkbird.com/tania/32/88_2.png) [@Tania](https://community.inkbird.com/u/Tania)
#### Post date: [April 19, 2024, 8:16am UTC](https://community.inkbird.com/t/itc-308-wifi-starting-cooling-cycle-too-early/150768/2 "2024-04-19T08:16:57Z")

</div>

Hello,  
Please understand that ITC-308-WIFI has a special temperature mode. Please let ITC-308-WIFI run for 2-3 cycles after the setup is completed. During this period, please do not perform any operations.  
Please refer to:

> [@Q&A: How does ITC-308WIFI work?](https://community.inkbird.com/t/q-a-how-does-itc-308wifi-work/151):
>
> ITC-308WIFI has a special temperature mode and a normal temperature mode. The trigger conditions for the special temperature mode are: Enter the setting mode through the SET key then exit. Enter the setting mode through the app then exit. In the special temperature mode, ITC-308WIFI will ignore the settings of HD (Heating hysteresis temperature) and CD (Cooling back temperature) and turn on the heating/cooling output. It will not enter the normal mode until the temperature reaches the SV tar…

---

<div class="post-metadata">

### Author: ![User\_1717257094878](https://avatars.discourse-cdn.com/v4/letter/u/ee59a6/32.png) [@User\_1717257094878](https://community.inkbird.com/u/User_1717257094878)
#### Post date: [June 1, 2024, 10:05pm UTC](https://community.inkbird.com/t/itc-308-wifi-starting-cooling-cycle-too-early/150768/3 "2024-06-01T22:05:16Z")

</div>

Hello, thank you for the comprehensive reply, this is exactly what I was looking for… Are you able to confirm if when setting up automation on the app, will the above issue occur each time? For example;

Day time SV: 25°C  
Night time SV: 20°C

As the parameters change every 12 hours, will this automatically put the unit into special temperature mode every 12 hours, or is special temperature mode ONLY activated when _user_ amendments occur?

Many thanks

---

<div class="post-metadata">

### Author: ![Tania](https://yyz1.discourse-cdn.com/flex031/user_avatar/community.inkbird.com/tania/32/88_2.png) [@Tania](https://community.inkbird.com/u/Tania)
#### Post date: [June 4, 2024, 2:48am UTC](https://community.inkbird.com/t/itc-308-wifi-starting-cooling-cycle-too-early/150768/4 "2024-06-04T02:48:40Z")

</div>

If the target temperature changes, it will be considered as a change of setting and will trigger the special temperature mode.