# ITC-100VH off set at 70 Celsius. Can I set the temp to turn back on at 65 Celsius?

**URL:** <https://community.inkbird.com/t/itc-100vh-off-set-at-70-celsius-can-i-set-the-temp-to-turn-back-on-at-65-celsius/165936>\
**Category:** Questions & Answers\
**Tags:** smart-controller\
**Created:** [July 18, 2024, 4:57am UTC](https://community.inkbird.com/t/itc-100vh-off-set-at-70-celsius-can-i-set-the-temp-to-turn-back-on-at-65-celsius/165936 "2024-07-18T04:57:34Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![phatteus](https://avatars.discourse-cdn.com/v4/letter/p/f475e1/32.png) [@phatteus](https://community.inkbird.com/u/phatteus)\
**Post date:** [July 18, 2024, 4:57am UTC](https://community.inkbird.com/t/itc-100vh-off-set-at-70-celsius-can-i-set-the-temp-to-turn-back-on-at-65-celsius/165936/1 "2024-07-18T04:57:34Z")

</div>

I have this PID set to cut the control current output at 70 degrees. Can I set it to turn back on at 65 degrees so that it does not cycle on and off a bunch of times?

---

<div class="post-metadata">

**Author:** ![Tania](https://yyz1.discourse-cdn.com/flex031/user_avatar/community.inkbird.com/tania/32/88_2.png) [@Tania](https://community.inkbird.com/u/Tania)\
**Post date:** [July 22, 2024, 8:02am UTC](https://community.inkbird.com/t/itc-100vh-off-set-at-70-celsius-can-i-set-the-temp-to-turn-back-on-at-65-celsius/165936/2 "2024-07-22T08:02:39Z")

</div>

Hello,  
Maybe you can see if the on/off mode meets your needs?  
SV=67.5 [calculate method: (70-65)/2 +65]  
dF=2.5  
CtrL=0  
Others are factory defaults.  
Working principle reference:  
 ![image](https://canada1.discourse-cdn.com/flex031/uploads/inkbird1/original/2X/7/7e71f86791dc0ba8035fb26081a07a6dd629dfa1.jpeg)